It is currently Tue Apr 21, 2026 7:34 am
 Post subject: Meter Center Series Ratings
PostPosted: Thu Apr 02, 2026 8:09 am
I’m working on a fault current calculation for a meter stack and had a question regarding series ratings.
According to the manufacturer, the Siemens QPH breaker can be series-rated with a Siemens 3VA6-H breaker, resulting in a load center feeder breaker with a 100kA AIC rating. Additionally, a Siemens QP breaker can be series-rated with a QPH breaker at 22kA.
My question is: if the feeder breaker (QPH) is part of a series combination rated at 100kA with the upstream 3VA6, can the downstream branch breakers (QP) also be considered as having a 100kA series rating? Or are they still limited to their own tested series rating (22kA with QPH)?
 Post subject: Re: Meter Center Series Ratings
PostPosted: Thu Apr 02, 2026 8:51 am
You would have to look in Siemens tables to see if the breakers "stack". However, I doubt it...best to double check.
Mike
PostPosted: Fri Apr 03, 2026 4:07 am
75kA available looks pretty high but not enough info to really evaluate. Are you confident in that value?
Also what Mike said RE: series ratings. Eaton has some info on tenant rating like what you have there with 3 breakers but the answer is what Mike said. You might be ok if the QP also has a rating with the 3VA6 but you'll need to look it up.
From Eaton. Siemens may be different:
SKM jockey for hire
PE in 17 states
