THE CABLE GUY wrote:
:
The IT guy unplugs the computer to remove for service or works on it in the enclosure. The safety person wants to know if that is enough as far as safety.
Unplugged, no safety required, however ESD controls should be used.
THE CABLE GUY wrote:
:My reply is as long as he does not touch any exposed conductors. Does he need electrical rated gloves? That does not seem feasible.
120V falls under the avoid contact rule, as long as he does not touch (or any conductive object he is holding) no gloves are required, if contact may be made, class 00 gloves shoul dbe worn for 120V.
THE CABLE GUY wrote:
:The safety person thinks it’s a mistake to put a warning label on such electrical enclosures containing industrial computers and devices what is the consensus?
.
Not a mistake at all, a little "over safe" if anything but I would do the same thing you are doing.