It is currently Thu Oct 22, 2026 5:31 am
Do you use the normal fault current only or consider alternate scenarios?
Normal Short Circuit Current Only 16%  16%  [ 14 ]
Consider Alternate Scenarios 84%  84%  [ 75 ]
None of the above 0%  0%  [ 0 ]
Total votes : 89
 Post subject: Utility Short Circuit Current
PostPosted: Sun Aug 29, 2010 4:00 pm
When performing an arc flash calculation study do you use the normal condition fault current only or do you also look at alternate scenarios such as minimum or maximum fault current?
PostPosted: Mon Aug 30, 2010 8:42 am
I voted that we consider alternate scenarios, but this is for (NESC) OH utility distribution lines where work will be performed at locations certainly other than the substation bus.
PostPosted: Wed Oct 06, 2010 9:53 pm
I have manipulated the local PUD substation power transformers on and off line (only within the software :p ) to affect highest and lowest available fault current. This did not affect most locations on this particular study buy perhaps a dozen out of 400 busses increased arc flash exposure when fault current was lowest.
Most locations I would not have access to information to do this but at this one spot I had previously completed work for the PUD.
