smokegetsnureyes wrote:
I am an instructor for a utility and have to teach arc flash / electrical safety training. We have not performed an arc flash analysis at many of our facilities as of yet. I have been using the table methods to inform the plant personnel as to what level of clothing to wear and at what distances to set up their boundaries. A study was recently completed at one of our facilities and several of the low voltage switchgears (<600V) ended up with 85cal/cm ratings.
Sounds like you may have not been using the tables correctly, does your system meet the limits of the tables in the notes? With 85cal/cm2 it does not sound like it.
smokegetsnureyes wrote:
The company that performed the analysis also provided the labels for each of our switchgears and MCC's. The labels on several of the swtichgears indicate Required PPE: Dangerous as well as No FR Category Found. I have noticed that their are 100cal/cm suits in the FR catalogs that I have looked through. Is it unacceptable to work on this equipment (e.g. racking breakers in or out) unless it is deenergized?
>40cal/cm2 the issue becomes the pressure from the arc, which has been found to be un-surviable at those levels, regardless of PPE being worn. However, this is from a note in the handbook and there is not a hard "rule" about this.
smokegetsnureyes wrote:
Can a 100cal/cm suit be utilized or is it unacceptable to work on this equipment at all unless it is deenegized. All electrical equipment is considered energized, until proven otherwise. How do I test it, while performing the task of testing would put me in harm's way. The flash hazard boundary for this same piece of apparatus is 242 inches. I don't have a long enough pole to reach it for testing since I have to have on proper PPE to be within the boundary. Does anyone know what to do in this case?
The verification that systems like this are de-energized is one of those issues where you are in a tough situation. You can re-calulate youe Ei at a distance other than what was assumed based on the length of your hotsticks.
Operating and racking of breakers can be done outside that 242" boundary with remote racking and switching devices, but sounds like you need to look at mitigation solutions.