It is currently Thu Oct 08, 2026 5:27 pm
Do you use current limiting devices to reduce the arc flash incident energy?
Yes 43%  43%  [ 30 ]
No 57%  57%  [ 39 ]
Total votes : 69
 Post subject: Current Limiting Devices
PostPosted: Sun Jan 09, 2011 6:05 pm
PostPosted: Mon Jan 17, 2011 1:56 am
Which current limiting products to reduce arc Flash risk ??
Which current limiting products are allowed for arc flash reduction ?
Do they request to succed some tests ?
PostPosted: Mon Jan 17, 2011 10:54 am
Current Limiting Fuses and Breakers reduce the let through fault current. By reducing the fault current, you reduce the Incidend Energy (arc flash).
PostPosted: Mon Jan 17, 2011 2:24 pm
IEEE 1584 did some testing with current limiting fuses and published a few equations. Properly applied C.L. breakers and fuses can significantly reduce the incident energy.
