It is currently Tue Nov 24, 2026 6:07 am
 Post subject: Bus Duct Labeling
PostPosted: Wed Mar 30, 2011 4:35 am
I searched the labeling forum and didn't see this address but I apologize if I missed it someplace.
What is everyone doing for labeling on a bus duct? Labeling entire bus with the worst case AFH? Prominently marking bus where AFH changes and labeling each side accordingly?
PostPosted: Wed Mar 30, 2011 6:48 am
If it is not
likely to require examination, adjustment, servicing, or maintenance while energized
(NEC 110.16) then I don't see why it has to be labeled.
PostPosted: Wed Mar 30, 2011 6:58 am
Thank you but I was thinking of where there are bus duct plug ins and the possibly of disconnects being plugged in to the bus duct at various locations along the bust duct.
PostPosted: Wed Mar 30, 2011 7:26 am
I see a some labeling just on the incoming section. But, it seems most people label every 20-30 feet or so.
I have no customers that label busway with multiple incident energy values.
Our policy is to recommend the use the worst case for the run.
PostPosted: Wed Mar 30, 2011 11:53 am
We label every section of duct, both sides, with the worst case scenario IE.
 Post subject: Re: Bus Duct Labeling
PostPosted: Thu Jul 24, 2014 10:02 am
Anyone have new thoughts on this query?
PostPosted: Sun Jul 27, 2014 6:59 am
It has been awhile since this post and here is what I am doing:
1. Determine the worst case arc flash hazard on the bus duct which is usually at the end of the bus duct run.
2. Discuss with the client on what their preference is for labeling. This has been varied:
*one label at beginning junction box
*labels on each side alternating every X ft
*labels on beginning junction box and at the end of the bus duct.