It is currently Wed Oct 21, 2026 8:02 am
 Post subject: 63 kVA Transformer Secondary - Arc-Flash Hazard
PostPosted: Thu Aug 04, 2011 4:18 pm
A 415V switchboard is supplied from a 63 kVA, 22/0.433kV transformer ( %z = 3.2% ).
A 250A MCCB is installed at the transformer secondary terminals and provides the only primary protection for the switchboard.
The bolted three phase initial symmetrical rms short-circuit current at the switchboard is 2.26 kA ( due to Utility impedance in addition to the 63 kVA transformer impedance).
Based on the IEEE 1584 -2002/2004a formulas, 25mm gap ( see attached spreadsheet ) the arcing current through the 250A MCCB is 1.76 kA which would cause the MCCB to trip in approx. 20 sec.
After 20 sec, the resulting incident energy at a working distance of 500mm would accumulate to a “dangerous� incident energy of 87.7 Cal / cm². How realistic is this ?
ISSA Guideline 2011, 2nd edition (E)-electric arc 2011.pdf [2.06 MiB]
Downloaded 268 times
PostPosted: Thu Aug 04, 2011 4:21 pm
Incorrectly sized MCCB on 63kVA transformer
I forgot to mention that the 250A MCCB is too large to provide either overload or short-circuit protection, however my question concerns the arc-flash hazard.
PostPosted: Thu Aug 04, 2011 8:02 pm
Unless there are restrictions on the worker's movements, he is likely to move away from the arc in less than 20 seconds and not receive the full 87.7 cal/cm² energy. IEEE Std 1584 and NFPA 70E suggest that a 2 second limitation on the time if movements are not restricted.
PostPosted: Fri Aug 05, 2011 5:33 am
I'm curious to know which part of NFPA 70E talks about the 2 second cutoff.
I know it's in IEEE 1584 (subject to appreciation by the person doing the study), but I wasn't aware it was in NFPA 70E.
PostPosted: Fri Aug 05, 2011 9:48 am
You're right, it isn't in NFPA 70E. NFPA 70E doesn't specify how to calculate incident energy, but IEEE 1584 is one of the methods used in Annex D (which is not a part of the NFPA 70E requirements).
PostPosted: Mon Aug 08, 2011 7:05 pm
I think 20 seconds is more in the area of welding isn't it?? In electrical time, that is HUGE!!
