IEEE 1584, NFPA 70E and the “2-Second Arc Duration” Myth
Pregunta:
I’ve heard that an arc flash can’t last longer than two seconds. Is that true?
Short answer:
No! An arc flash can absolutely last longer than two seconds. Neither IEEE 1584 nor NFPA 70E says an arc flash is physically limited to two seconds. The two-second value is an assumption used for exposure time, not a limit on how long an arc can actually exist.
This misunderstanding comes from a statement in IEEE 1584-2018, which says that “2 seconds usually is a reasonable assumption for the arc duration.” That sentence gets quoted a lot, but it’s often taken out of context.
What IEEE 1584 is really addressing is how long to assume a worker is exposed to the arc, not how long the arc itself can physically exist.
What the 2-Second Assumption Actually Means
In an arc-flash study, arc duration is normally based on protective device clearing time—how long it takes a breaker, relay, or fuse to detect the fault and open the circuit. In some systems, especially where protective devices are slow or coordination is poor, that clearing time can exceed two seconds.
IEEE 1584 permits the arc duration to be capped at 2 seconds for calculation purposes only when it is reasonable to assume that a person can move out of the arc-flash exposure area. In other words:
  • The arc may still be burning
  • The equipment may still be energized
  • But the worker is assumed to no longer be in front of it
Two seconds represents human reaction and escape time, not a physical limit on arc duration. If there is a “boom”, we go into the fight or flight response and in this case, flight is the normal response, jumping out of the way.
Arc Flashes Can Last Much Longer
The actual arc duration is generally unpredictable and is a function of many factors such as arcing current, electrode gap, voltage and much more.  That is why the protective device clearing time is used – a known value.
In real-world conditions, an arc flash can potentially last:
  • Several seconds
  • Tens of seconds
  • Or until the equipment fails catastrophically or the power source is removed
This is especially true in systems with:
  • Failed or miscoordinated protection
  • Low arcing fault current resulting in protection having a long response time
  • Utility-fed equipment without fast local protection – only the upstream utility device.
You don’t have to dig very deep on YouTube to see videos of some very long duration arc flash events.
That’s why it’s incorrect—and dangerous—to think of two seconds as a hard limit.
How NFPA 70E Uses the Same Concept
NFPA 70E also references the two-second arc duration assumption in specific locations.
As an example, NFPA 70E Table 130.7(C)(15)(b), which provides arc-flash PPE categories for dc systems.
Nota informativa 2 to this table states that a two-second arc duration is assumed if there is no overcurrent protective device to limit the duration of the arc.
This language is often misunderstood. It does no mean:
  • The arc will self-extinguish after two seconds
  • dc arc flashes are limited to two seconds
  • Two seconds is inherently safe
What it means is that, for PPE category guidance, NFPA 70E assumes a two-second exposure duration when no overcurrent protective device exists to clear the fault. Often dc systems involve battery systems such as in uninterruptable power supplies (UPS) which often will not have overcurrent protection –
Caution! – technical humor follows.
  I’m sure this lack of protection has something to do with the “U” in the title – Uninterruptable.
NFPA 70E’s two-second assumption in Table 130.7(C)(15)(b) is a conservative exposure assumption, not a statement about arc behavior. Similar to ac arcs, a dc arc can potentially continue well beyond two seconds.
Engineering Judgment Is Required
The 2-second cap should only be used when it is realistic that a worker could recognize the event and physically move away.
Examples where the 2-second assumption may be reasonable:
  • Standing in front of open, accessible equipment
  • No physical restraints or confined space
  • Clear escape path
Examples where it may no be reasonable:
  • Working in a bucket truck
  • Working on electrical equipment in enclosed spaces
  • Similar situations that may restrict the worker’s ability to rapidly move away
If a worker cannot reasonably move away, then the actual protective device clearing time should be used, even if it exceeds two seconds.
Bottom Line
The 2-second value in IEEE 1584:
  • Is not a limit on arc duration
  • Is not a guarantee of safety
  • Is not automatic
It is a calculation assumption based on human response, and it should only be applied when justified. Used correctly, it helps prevent unrealistic energía incidente values. Used incorrectly, it can significantly underestimate arc-flash hazard
Acerca de Jim Phillips
With a career beginning in 1981 and Brainfiller launching in 1987, Jim has built a global reputation as a trusted leader in electrical safety.
He currently:
  • Serves on multiple electrical safety and standards committees, including Norma NFPA 70E, IEEE 1584, IEC TC78, and the National Electrical Code (CMP-4).
  • Has authored over 100 technical articles and has been a Contributing Editor for Electrical Contractor Magazine (NECA) since 2009.
  • Holds leadership positions in international working groups that shape arco eléctrico, live working, and risk assessment standards.
  • Has delivered keynotes and workshops in countries around the globe for engineers, utilities, and industrial organizations.
💡 Did you know? Many NFPA 70E trainers learn the material by attending Jim’s classes—while Jim is involved directly with the standards they teach.
Jim Phillips, P.E. presenting beside a large conference screen
Jim Phillips, P.E. presenting at an Arc Flash Electrical Safety event in Brisbane
NFPA 70E Training Courses Available Through Brainfiller
Brainfiller offers several courses designed and taught by Jim, all targeted to engineers, electricians, and safety professionals.
NFPA 70E Qualified Worker Training (8 hours)
Covers risk assessment, PPE, LOTO, establishing an electrically safe work condition, and auditing requirements.
How to Perform an Arc-Flash Study | IEEE 1584 (16 hours)
Modeling, arcing current, incident energy, arc-flash boundaries, and system-level mitigation.
Fundamentals of Electrical Safety (2 hours)
Shock hazards, arc-flash basics, and the building blocks behind NFPA 70E.
DC Electrical Safety Fundamentals (2 hours)
Key safety practices for data centers and DC systems.
All training is available live, on-site, or on-demand, and includes completion certificates with CEU/PDH documentation.
Proven Results and Industry Recognition
Organizations that adopt Jim’s training consistently report:
  • Stronger safety culture
  • Fewer electrical incidents
  • More confident teams
  • Cleaner audits
  • Better PPE and risk-assessment decisions
Recent recognition includes:
  • IEEE PCIC Prize Paper Award (2024)
  • NFPA/IEEE Research Project Recognition (2022)
  • Electrical Safety Excellence Award (2020)
Conference attendees talking in a reception area
Jim Phillips, P.E. with colleagues holding awards at a professional conference
How Jim Stays Ahead of Developing Safety Trends
Because Jim is embedded in NFPA, IEEE, IEC, and NEC committees, he sees emerging trends before they appear in the codebook.
His training materials are updated immediately after each standards cycle, keeping teams aligned with Norma NFPA 70E, IEEE 1584, and OSHA expectations.
🔧 From code to craft: Jim explains why requirements exist and how to apply them correctly in real electrical systems.
Benefits of Choosing Jim Phillips and Brainfiller
  • Direct insight from a standards insider
  • Reduced incidents and stronger compliance
  • Consistent updates in line with every NFPA 70E cycle
  • Flexible learning formats
  • Practical, defensible training grounded in real-world conditions
Partnering with Jim Phillips ensures your team learns NFPA 70E and arc-flash safety from someone who has helped guide the direction of the standard—not from copied material.
Elevate Your Electrical Safety Program
Train with Jim Phillips through Brainfiller.
Empower your team, strengthen compliance, and protect lives with industry-leading NFPA 70E and arc-flash training.