 Post subject: DC Arc flash boundary
PostPosted: Thu Oct 20, 2016 8:13 pm 

Joined: Mon Jan 31, 2011 2:53 pm
Posts: 12
Could i use the (DB) empirically derived model equation of IEEE Std 1584-2002 to calculate the Flash-protection boundary (for box configurations) and the Lee (DB) equation (for open air configurations)?

I can´t find a equation for DC Arc flash boundary.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc flash boundary
PostPosted: Thu Oct 20, 2016 8:46 pm 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
consider using equations 11 and 13 from http://arcadvisor.com/faq/dc-arc-flash- ... y-modeling for dc arc in open and arc in a box respectively.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc flash boundary
PostPosted: Mon Oct 24, 2016 9:57 pm 

Joined: Mon Jan 31, 2011 2:53 pm
Posts: 12
Thanks arcad for the equations. I read the IEEE 1584 again, and i have found that the AFB depends of the equation used to calculate the incident energy. In this case your equation its ok for me.


Top
 Profile Send private message  
Reply with quote  
 Post subject: Re: DC Arc flash boundary
PostPosted: Tue Oct 25, 2016 8:03 pm 
Sparks Level
User avatar

Joined: Wed Jun 10, 2009 5:00 pm
Posts: 271
Location: Toronto
No prob, mauricioville. FYI, this calculation procedure has been coded in DCAFA V3.0 software program and is very similar to the procedure proposed by Jim Phillips in Know Your Arc: DC arc flash calculations. It also takes into account circuit time constant when determining arc duration as a function of predicted arcing current, upstream protection device type and rating, and the fault time constant.

_________________
Michael Furtak, C.E.T.
http://arcadvisor.com


Last edited by wbd on Wed Oct 26, 2016 3:39 am, edited 1 time in total.
Deleted links to commercial website


Top
 Profile Send private message  
Reply with quote  
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
© 2022-2025 Arcflash Forum / Brainfiller, Inc. | P.O. Box 12024 | Scottsdale, AZ 85267 USA | 800-874-8883