It is currently Sun Nov 22, 2026 3:49 pm
 Post subject: DC Arc flash boundary
PostPosted: Thu Oct 20, 2016 8:13 pm
Could i use the (DB) empirically derived model equation of IEEE Std 1584-2002 to calculate the Flash-protection boundary (for box configurations) and the Lee (DB) equation (for open air configurations)?
I can´t find a equation for DC Arc flash boundary.
 Post subject: Re: DC Arc flash boundary
PostPosted: Thu Oct 20, 2016 8:46 pm
consider using equations 11 and 13 from http://arcadvisor.com/faq/dc-arc-flash- ... y-modeling for dc arc in open and arc in a box respectively.
Michael Furtak, C.E.T.
PostPosted: Mon Oct 24, 2016 9:57 pm
Thanks arcad for the equations. I read the IEEE 1584 again, and i have found that the AFB depends of the equation used to calculate the incident energy. In this case your equation its ok for me.
PostPosted: Tue Oct 25, 2016 8:03 pm
No prob, mauricioville. FYI, this calculation procedure has been coded in DCAFA V3.0 software program and is very similar to the procedure proposed by Jim Phillips in Know Your Arc: DC arc flash calculations. It also takes into account circuit time constant when determining arc duration as a function of predicted arcing current, upstream protection device type and rating, and the fault time constant.
Deleted links to commercial website
