With the awareness of arc flash, many giant manufacturers do not manufacture the Service Disconnect and the Automatic Transfer Switch located in the same section or enclosure. However, this practice can be seen in the field for switchboards rated as high as 600 Amps.
The dangerous part is the upstream of service disconnect is like a blind spot as the only protective device is the utility’s fuse on the primary side of the transformer and often result in high incident energy (greater than 40 Cal/cm2 in most of the cases) at the service disconnect. But because of service disconnect as protective device, in the downstream the incident energy on the ATS(normal-utility side) gets reduced to for instance less than 4 cal/cm2. The problem is although ATS has lower incident energy, it is located right below the Service Disconnect in the same section (enclosure). This is a arc flash hazard and I affix the conservative label (service disconnect) on the section that has service disconnect on the top and ATS at the bottom. So please share your thoughts on how you affix labels:
1. When the Service Disconnect & ATS is located in the same section (enclosure)
2. When there is a barrier between Service Disconnect and ATS located in the same section (enclosure).