Electrode Configuration and 2018 IEEE 1584
Electrode Configurations Grey MatterThe most frequently asked question that I receive regarding the 2018 edition of IEEE 1584 is:
“How do I determine the electrode configuration?”
The 2002 edition was based on arc flash tests with the electrodes oriented in a vertical configuration. When performing an arc flash study based on the 2002 edition, there were only two options available – an arc flash in an enclosure and an arc flash in open air – both based on a vertical electrode configuration.
Since the original 2002 edition was published, additional research has shown that incident energy can be influenced by the electrode configuration.  As a result, many new tests were conducted using additional new electrode configurations including vertical electrodes that terminate into an insulating barrier as well as horizontal electrodes in an enclosure/box and in air.  This is in addition to the original vertical configurations in an enclosure and in air.  The additional configurations and the resulting
new calculation methods make it possible to provide more detailed modeling of electrical equipment.
With the original vertical electrode configuration, when an arc flash occurs in an enclosure, the arc is driven away from the source, down the electrodes and towards the bottom of the box and spills out of the front. Research has demonstrated that if vertical electrodes are terminated into an insulating barrier, the arc hits the barrier and the plasma cloud is directed more towards the enclosure opening.
When the electrodes are placed horizontally, the arc plasma is directed from the ends of the electrodes outward.
In addition, tests were also conducted in open air and included the original vertical configuration in open air and a new configuration with horizontal electrodes in open air.
To provide greater modeling flexibility for equipment, five different electrode/bus configurations are now included in the 2018 Edition of IEEE 1584 which include:
Figure 1: VCB – Vertical conductors / electrodes in a metal box/enclosure (also in 2002 Edition)
Figure 2: VCCB – Vertical conductors / electrodes terminated in an insulating barrier in a metal box / enclosure
Figure 3: HCB – Horizontal conductors / electrodes in a metal box / enclosure
Figure 4: VOA – Vertical conductors / electrodes in open air (also in 2002 Edition)
Figure 5: HOA – Horizontal  conductors / electrodes in open air
Confusion and Uncertainty
At the present time, the new standard is only a few months old and people are trying to determine what to make of it.  This problem (and confusion and uncertainty) is not new.  A similar situation occurred when the original 2002 edition of IEEE 1584 was first released.  People found themselves trying to sort out the details of how to use the new concepts.
Some of the initial uncertainty and confusion were questions such as: Do you measure the actual bus gaps or use the defaults from IEEE 1584 that were also included in arc flash software.  Do you dare cut the arc duration off at 2 seconds? – Most people did not use 2 seconds in the early days.  How much detail was really necessary. The list went on. These questions may seem trivial today but at the time they were considered quite significant.
Over time, the industry converged into a more standardized practice.  The website: ArcFlashForum.com  which began in 2007 also helped out a bit.  Each week, I would ask a survey question known simply as “Question of the Week” to gauge how people were addressing certain issues.  Keep in mind this was long before the social media platforms that exist today.  Questions about labeling and colors/signal words, working distance, conductor gaps, and years of similar questions, helped others realize they were not alone and could see how others were addressing certain issues.
With the introduction of the 2018 Edition of IEEE 1584, I am at it again with the “Question of the Week.”  A few questions have already been asked about specific issues regarding 2018 IEEE 1584 but the biggest one is how to address the electrode configuration. It is a new concept and with anything new comes second guessing, uncertainty and confusion.
Arc Flash Forum – Electrode Configuration Collaboration
This past week, Electrode Configuration was the subject of the “Question of the Week” at ArcFlashForum.com
The question was:
How will you/consultant/company address electrode configurations?
Although far from a scientific survey, the choices and results at this moment in time were:
  • Use VCB/VOA for now – same as 2002 edition: 17%
  • Review actual equipment bus/conductor configuration and decide: 39%
  • Use the configuration that provides highest incident energy: 5%
  • Something else: 0%
  • Not sure yet: 39%
So far there seems to be a tie between “Review actual equipment bus/conductor configuration” and “Not sure yet.”  The “Not sure yet” group is simply history repeating itself as was the case in 2002.
Collaboration – Help Wanted!
To assist people in determining electrode configurations for equipment, a new section has been added to the ArcFlashForum.com   It is known as:
 “Electrode Configurations – 2018 IEEE 1584”
Here people can post photos of various types of equipment for the users to discuss and analyze what the possible configurations may be.
The goal is to develop a public library of equipment and configurations to help others.  The 2018 edition of IEEE 1584 has many new options available for arc flash modeling.  Now it’s time to sort it all out!