Question:
Some arc-flash labels list the arc-flash boundary in inches, others in millimeters or meters, and some even show odd values like 3.4 feet. On top of that, IEEE 1584 uses joules per square centimeter (J/cm²), but PPE ratings are in calories per square centimeter (cal/cm²). Why is there so much inconsistency on NFPA 70E arc flash / equipment labels?

Answer:
It looks messy, but there’s a logical reason behind it. The short version is this: IEEE 1584 is based on metric units, and the end user prefers imperial units (inches etc.) for NFPA 70E labels. However, the units used on arc flash labels still seem to vary widely

IEEE 1584 Is Metric by Requirement

IEEE as well as many other standards requires the use of the metric system in its equations. As a result, IEEE 1584:

  • Arc-flash boundary distances are calculated in millimeters
  • Incident energy is calculated in joules per square centimeter (J/cm²)

This isn’t optional. IEEE standards are written to be internationally applicable, and the metric system is required for consistency. It should be noted that IEEE 1584 is a global standard and some countries or regions do prefer metric units.

So when an arc-flash study is performed, the raw calculation results coming out of IEEE 1584 are always metric — even if you never see those units on the final report or label.

Why Labels Show Inches, Feet, or Decimals

NFPA 70E does not mandate a specific unit system for arc-flash labels. What NFPA 70E 130.5(H) does require is that electrical equipment be labeled with meaningful arc-flash information so workers can recognize the hazard and take appropriate protective measures.

To meet that requirement, arc-flash software typically converts:

  • Millimeters into inches, feet, or meters
  • Based on user preference, company standards, or regional practice

That’s why you may see:

  • 42 inches on one NFPA 70E label
  • 1.1 meters on another
  • 3.5 feet on a third

The math is correct — it just wasn’t rounded to a “nice” number after conversion. From an NFPA 70E standpoint, that’s acceptable as long as the information is accurate and clearly communicated.

Incident Energy: J/cm² vs cal/cm²

The same issue shows up with incident energy.

IEEE 1584 is used to calculate incident energy in J/cm², where:

  • One joule equals one watt-second

However, PPE Ratings defined by standards such as ASTM and IEC and referenced in NFPA 70E are based on cal/cm², and arc-rated clothing and face shields are tested and labeled in those units.

Because NFPA 70E requires PPE selection based on incident energy exposure, arc-flash software converts:

  • J/cm² into cal/cm²
  • So the value on the NFPA 70E label matches PPE ratings and hazard categories

Again, the inconsistency isn’t an error — it’s a necessary translation between calculation standards and safety requirements.

What NFPA 70E Actually Cares About

NFPA 70E 130.5(H) doesn’t care whether a distance is shown in inches, feet, or meters. It cares that:

  • The arc-flash boundary is clearly identified
  • The incident energy or PPE information is accurate
  • The label supports the arc-flash risk assessment

As long as the label addresses the requirements of NFPA 70E 130.5(H) and aligns with the arc-flash study, the units are technically a secondary concern.

The Real Problem: Confusion, Not Conversion

Where this becomes an issue is worker interpretation. A label that mixes unfamiliar units or odd decimal values can:

  • Slow down decision-making
  • Increase the chance of misreading a boundary
  • Reduce confidence in the NFPA 70E labeling program

That’s why many companies standardize:

  • One distance unit system
  • One rounding convention
  • One label format across the facility

This isn’t required by NFPA 70E — but it’s often a very good idea.

Bottom Line

The unit differences on arc-flash labels exist because:

  • IEEE 1584 requires metric units
  • NFPA 70E requires usable safety information
  • Software bridges the gap by converting units for labels

As long as the label meets NFPA 70E 130.5(H) requirements and accurately reflects the arc-flash study, the units are technically correct — even if they don’t always look consistent.

Jim Phillips, P.E. presenting beside a large conference screen
Jim Phillips, P.E. presenting at an Arc Flash Electrical Safety event in Brisbane

How 45 Years of Experience Built Jim’s NFPA 70E and IEEE 1584 Expertise

Jim Phillips is an internationally recognized authority in electrical power systems, arc-flash analysis, and electrical safety, with more than four decades of professional experience. He has delivered over 3,000 training programs worldwide, educating tens of thousands of people from all seven continents, (Yes, Antarctica is included!) Known for his clear, engaging presentation style, Jim is widely regarded as one of the industry’s leading trainers and public speakers.

His professional background spans transmission system planning; industrial, commercial, and utility power system design and analysis; co-generation plant design; and forensic engineering investigations. He is also frequently engaged as an expert witness in matters involving electrical power systems and arc-flash hazards

  • Founder and President Brainfiller.com
  • Founder ArcFlashForum.com
  • Associate Director | Electrical Safety UK, Ltd. – Rotherham, UK
  • Contributing Editor | Award Winning NECA Magazine Electrical Contractor

Arc Flash and Standards Committees Leadership

For decades, Jim Phillips has been actively involved with U.S. and international standards development.  This includes:

  • Vice Chair: IEEE 1584 – IEEE Guide for Performing Arc-Flash Hazard Calculations
  • International Chair Emeritus: IEC TC78 – International Live Working and Arc Flash Standards
  • Chair: IEEE PCIC Electrical Safety Subcommittee
  • Technical Committee Member: NFPA 70E Standard for Electrical Safety in the Workplace
  • Technical Committee Member: National Electrical Code – CMP 4
  • Steering Committee: IEEE/NFPA Arc Flash Collaborative Research Project
Arc Flash investigation
Fukushima after Arc Flash

NFPA 70E Training Courses Available Through Brainfiller

Brainfiller offers several courses designed and taught by Jim, all targeted to engineers, electricians, and safety professionals.

NFPA 70E Qualified Worker Training (8 hours)

Covers risk assessment, PPE, LOTO, establishing an electrically safe work condition, and auditing requirements.

How to Perform an Arc-Flash Study | IEEE 1584 (16 hours)

Modeling, arcing current, incident energy, arc-flash boundaries, and system-level mitigation.

Fundamentals of Electrical Safety (2 hours)

Shock hazards, arc-flash basics, and the building blocks behind NFPA 70E.

DC Electrical Safety Fundamentals (2 hours)

Key safety practices for data centers and DC systems.

All training is available live, on-site, or on-demand, and includes completion certificates with CEU/PDH documentation.

Elevate Your Electrical Safety Program

Train with Jim Phillips through Brainfiller.
Empower your team, strengthen compliance, and protect lives with industry-leading NFPA 70E and IEEE 1584 arc-flash training.

You may also be interested in…